Created 4/08/09
This week I was going to write about one of the topics that generate a lot of disagreement among folding trailer owners – the BAL leveler. However, that will have to wait for a while as another item surfaced and I discovered it generated more debate than comparing a BAL Leveler to wood or Lynx blocks. This all started when a fellow camper ask if he needed to ground his Honda EU3000 generator. He had a grounding bolt but wasn’t’ sure if he should use it. Well I have the same generator and had seen the grounding bolt but I never did any research on the topic.
So it was off to Google and a search on “Generator Grounding” gave me almost a million hits. One of the first documents I read - made it very simple"... most people do not properly ground their portable generations as per code and manufacture's instructions."
So if the code requires it then I need to ground mine. Right?
Well not exactly. Let's read the code:
National Electrical Code (NEC) 250.34 Generators-Portable and Vehicle-Mounted
(A) Portable Generators. The frame of a portable generator is not required to be grounded to the earth if:
(1) The generator only supplies equipment or cord-and-plug-connected equipment through receptacles mounted on the generator, or both, and
(2) The metal parts of generator and the grounding terminals of the receptacles are bonded to the generator frame.
Did I read that right? I’m using cord-and-plug-connected equipment and I know my generator had the metal parts and grounding terminal bonded to the generator frame… so I don’t need to ground my generator.
However, as I continued to read I discovered that there were some of my fellow campers who for safety reasons thought that grounding was required. So I wonder what OSHA had to say?
Under conditions that are the same as the NEC, “ OSHA directs (29 CFR 1926.404(f)(3)(i)) that the frame of a portable generator need not be grounded (connected to earth) and that the frame may serve as the ground (in place of the earth).
Thus, rather than connect to a grounding electrode system, such as a driven ground rod, the generator’s frame replaces the grounding electrode. If these conditions do not exist, then a grounding electrode, such as a ground rod, is required.”
Now there are some folks that do ground their generators. However, to be correctly grounded you need an 8 foot grounded rod - which would be impossible to either put in or take out of the ground at a camp site. And a short metal spike is not good enough and actually is against code. In addition, some jurisdictions it is "illegal to dig or drive a ground rod in the ground unless you first call the local utilities and request a survey of the area".
Note – the above applies to portable generator such as those in folding trailers. If the generator is mounted on a vehicle (as is the case of some motor homes or travel trailers) then NEC requires that the generator frame be bonded to the vehicle frame.
Ruide